jean vallee
8/22/2016
Have a 18x18 shed roof planned for attached screen porch. Can't be higher pitch due to 2nd story window. I will have 24" oc rafters and cdx roof deck with ice/water shield and insulation. looking at metal shingles as well as vertical standing seam. budget is an issue but I don't want exposed fasteners. Am I looking at the right options?
Todd Miller
Classic Products, Inc.
8/22/2016
The only metal product approved for that low of pitch will be a mechanically seamed standing seam. You might "get by" with a minimum 1.5" tall seam snap lock standing seam with sealant in the locks. No way I'd use metal shingles on that pitch.
Info @windowsonwashington.net
An informed customer is our best customer.
8/23/2016
+1 Mechanical double lock is going to be your best application here and as Todd stated, nothing in the metal shingle family will work.
Kerry Moore
5/10/2017
I have a client who has a simple gabled roof with solid decking and dimensional shingles with a ridge vent, He is looking to go with standing seam. Back side is 2:12 pitch. Front side is 1:12 pitch till about six feet from the ridge. At that point it changes slightly to a 2:12 pitch. I see the reply above about snap lock. You don't mention a trapezoid shaped seam, or seam height. Any limitations?
Info @windowsonwashington.net
An informed customer is our best customer.
5/10/2017
1:12 it will have to be a mechanical seamed roof.