I had a small two stall barn structure added on to an existing structure, and in winter i notice alot of condensation that drips all over.!! The horses warm the air against the cold roof, which has a very slow slop. I tried commercial spray foam, and had no success...please help,. Hoping to not have to replace entire roof.!!
Or copy this URL:
https://www.metalroofing.com/spirit/comment/14422/find/
You need more insulation value in the roof and some sort of non-permeable barrier (if closed cell foam, not required).
If that is not an option, you will need to ventilate that warm moist air from accumulating along the roof line.
http://www.buildingscience.com/documents/digests/bsd-119-summer-condensation-problems-in-ice-arenas?full_view=1
Eric Novotny An informed customer is the Best Customer!
1/26/2010