Planning on attaching a 20' x 30' lean-to cover on an existing concrete block building. It will have to attach under the eve. Are there special parts available to place against the wall to keep the wind blown rain from leaking and running down the wall?
Or copy this URL:
https://www.metalroofing.com/spirit/comment/13807/find/
The best solution is to make a saw cut into the block wall about an inch deep. Then inject some urethane caulk into the saw cut and insert a reglet flashing, which would overlap a high eave flashing.