Quick question, is it possible to use a standing seam roof on a flat roof (slope 1/4" per 1'-0") or what is the min. slope allow for a standing seam roof.
Thanks
Guest User
2006-03-23 12:11:59.000000
Can you provide an example, such as a manufacturer and product style or number.
I have a slightly pitched flat roof situation that I am hoping to use a metal solution on.
THanks
Guest User
2006-12-25 13:46:15.000000
Most standing seams require a 3:12 pitch. However, there are field-seamed (aka mechanical seamed) standing seam roofs which can be use don pitches as low as 1/8:12.
Todd Miller
2006-03-23 23:07:57.000000
Go back to our web site and you can research the various profiles by manufacturer and contact them.