Could you tell me what the minimum pitch on a standing seam roof safely would be? We are doing a residential project where we would like a minimal pitch.
Thanks for your help.
Or copy this URL:
https://www.metalroofing.com/spirit/comment/6013/find/
There are many different styles of standing seam. Generally, though, most systems best-suited for residential use require at least a 3:12 pitch. However, there are standing seam systems, especially those used on industrial buildings, suitable for roof pitches as low as 1/4:12.
Do not ever use a roofing product at a pitch lower than the minimum pitched required by its manufacturer.
Or copy this URL:
https://www.metalroofing.com/spirit/comment/6015/find/
I visited their website and looked at the Easy Lock panel. There is some uniqueness to it which I am sure supports that low of a minimum pitch.
I would ask them for any tests results they have as well as to speak with past customers.
Keep in mind that Easy Lock does not install with clips so it is limited in terms of its allowance for expansion and contraction -- proper fastener placement will be critical.